Evening, I have a question if I may. If I have in my garage a 2way DB with a 63 amp rcd fed from main board in house on a 32a mcb but rcd protected. If I perform an auto rcd test would I be right in thinking it would trip the main board 1st as it’s rated at 32amp?

thank you
 
No. You would be testing the RCD in magnitudes of mA.
The 63A rating is the maximum current rating to be drawn through the device during normal service.

Assuming both RCDs are 30mA either or both could trip when testing the downstream RCD.
 
No. You would be testing the RCD in magnitudes of mA.
The 63A rating is the maximum current rating to be drawn through the device during normal service.

Assuming both RCDs are 30mA either or both could trip when testing the downstream RCD.
Thank you for your reply, other than a mechanical check on the 63 amp in the garage dB how else could it be checked without/bypassing the main board one. Or is it not necessary as long as one or the other goes?.
 
Thank you for your reply, other than a mechanical check on the 63 amp in the garage dB how else could it be checked without/bypassing the main board one. Or is it not necessary as long as one or the other goes?.

Having two RCDs in line with each other like this is bad design and gives no selectivity. The only way to test the garage board RCD properly would be to bypass the supplying RCD, but this would not be recommended if it meant energising a circuit that should have RCD protection if you had removed it.

So short answer is that you can't effectively test the RCD in the current arrangement. Unless you get lucky and only the garage one trips.
 
Having two RCDs in line with each other like this is bad design and gives no selectivity. The only way to test the garage board RCD properly would be to bypass the supplying RCD, but this would not be recommended if it meant energising a circuit that should have RCD protection if you had removed it.

So short answer is that you can't effectively test the RCD in the current arrangement. Unless you get lucky and only the garage one trips.
Thank you for taking the time to answer this for me.
 

Reply to Selectivity in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
886
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks for all comments still debating how to solve this, i personally would install MCB, having an idea the cable is installed under...
Replies
11
Views
2K
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
837

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top