In the CFP alarm sense manual, the circuit showing the alarm sense sounders shows + - at the sounders.
I just took this to indicate the sounders were polarity conscious, although it doesn't actually say this. Says to look at the manuals for each device.

Just looked on the C-tec website, your right they're not polarity conscious. In answer to your earlier question, it looks like all 5500 series sounders are compatible.
 
Last edited by a moderator:
@tazz would be the man in the know... from what I've read the sounders must be polarised they sit at a voltage between 9V-15V when quiescent and when the voltage rises above 20V the sounders activate.
 
In the CFP alarm sense manual, the circuit showing the alarm sense sounders shows + - at the sounders.
I just took this to indicate the sounders were polarity conscious, although it doesn't actually say this. Says to look at the manuals for each device.

Just looked on the C-tec website, your right they're not polarity conscious. In answer to your earlier question, it looks like all 5500 series sounders are compatible.
Thanks
 

Are both showing faulty or just 1 ?

Just read your post in reply to Lee, you mention End of line resistance ?
The manual I've got, shows 0.47uf 50v End of line Capacitors on the sense circuits.
The 6k8 resistors are for when you install conventional sounder circuits.
 
Last edited by a moderator:
Are you using Apollo Alarm Sense or are you using a 2 wire system.
If your using a 2 wire system then the sounders must be wired reverse polarity. All fire alarms weather on sounder circuits or combined zone circuit, change polarity when in alarm status, this is why bells etc have blocking diodes. Can you state the panel and exact equipment your using
 
Are you using Apollo Alarm Sense or are you using a 2 wire system.
If your using a 2 wire system then the sounders must be wired reverse polarity. All fire alarms weather on sounder circuits or combined zone circuit, change polarity when in alarm status, this is why bells etc have blocking diodes. Can you state the panel and exact equipment your using
do they have to be wired in reverse? I was reading this link which said they are operated on voltage. Apollo Fire - 55000-017APO - AlarmSense Open-Area Sounder Visual Indicator - https://www.apollo-fire.co.uk/products/range/alarmsense/sounder-visual-indicators/55000-017apo-alarmsense-open-area-sounder-visual
 

Reply to the thread, titled "Sense alarm Fire alarm" which is posted in Security Alarms, Door Entry and CCTV (Public) on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top