Dear Members,
Seeking your view to assess a risk for replacement one length of PVC/SWA/PVC Cable.
Back Ground:
A 90 KW Motor is connected to Star-Delta Starter in MCC at a distance of 200 meters, by 2 runs of 3-core70 mm2 PVC/SWA/PVC cables buried directly underground.
One length having an underground joint covered in concrete recently develops earth fault, one core shorted to ground.
Intend to replace only one length of 3-core faulty cable, laying on surface cable tray that carries other small power and control cables in stead of underground due to majority length of existing cable route already covered by concrete.
Concerns:
Will separate run cable on surface mounted cable creates eddy current since it is not bundled with the other length of cable?
The existing galvanized metal cable tray has metal cover of most of its length.
Thanks,
chlee-penang
Seeking your view to assess a risk for replacement one length of PVC/SWA/PVC Cable.
Back Ground:
A 90 KW Motor is connected to Star-Delta Starter in MCC at a distance of 200 meters, by 2 runs of 3-core70 mm2 PVC/SWA/PVC cables buried directly underground.
One length having an underground joint covered in concrete recently develops earth fault, one core shorted to ground.
Intend to replace only one length of 3-core faulty cable, laying on surface cable tray that carries other small power and control cables in stead of underground due to majority length of existing cable route already covered by concrete.
Concerns:
Will separate run cable on surface mounted cable creates eddy current since it is not bundled with the other length of cable?
The existing galvanized metal cable tray has metal cover of most of its length.
Thanks,
chlee-penang