hi

when running a 10mm bonding( seperate to the cpc proctected distribution circuit) conductor for a pme supply to a detached garage that contains (water/gas services) is it ok to run from exisitng house cu to gargae cu and then bond the services to garage cu. or does the bonding conductor have to be unbroken all the way back to the house cu

many thnaks
 
if you are using the house earthing for the garage then the extraneous metalwork in the garage needs to be bonded to the house MET ( min 10mm )
 
hi

when running a 10mm bonding( seperate to the cpc proctected distribution circuit) conductor for a pme supply to a detached garage that contains (water/gas services) is it ok to run from exisitng house cu to gargae cu and then bond the services to garage cu. or does the bonding conductor have to be unbroken all the way back to the house cu

many thnaks
Yes it is.
The two earth bars in the CUs become Earth Marshalling Terminals.
No the conductor doesn't have to be unbroken back to the house CU, or to the MET.
 
directly from met to each service ( water, gas,steel framework), or can you run a 10mm bonding conductor to garage cu and then bond garage extrenous conductive parts to the garage cu
yes...there nothing to say that the seperate 10mm earthing conductor to the C/U in the garage cant be the PME that you export....
 
so if you export the pme to the garage CU via the seperate 10mm bonding conductor would you only earth the supply cable at the house cu and not terminate at the garage cu ???? or just connect the supply earth as well
 
Last edited:
i take it your running armoured to the garage..?..yes?....if so then earth the armourings at the house end only......then use the CPC of the armoured together with the seperate 10mm earth cable together...parrallel em up..both ends...into the garage C/Us MET....then take the 10mm earthing cable you exported from there to extranious conductive parts within the garage..(water and gas)......keep it continuous...that is to say you go to the first extranious point...lets say gas....bare the cables insulation off....enough to terminate into a BS951 clamp..BUT DONT CUT IT...KEEP IT CONTINUOUS...then from there to the water...or vice versa...from water to gas...depends which service is nearer to the garage C/U of course...
 
One of the problems with using both the armour and the bonding conductor jointly, is that you would have to guarantee that the armour is of a sufficient CSA to withstand the unknown current that may flow in it.
You would also have to guarantee that the circuit conductors would not suffer from the increased temperature caused by the unknown current flowing in the armour.
 
wouldnt use the armour for the cpc or main bonding conductor. would use either seperate 10mm main bonding conductor or use the cpc (3rd core of the swa if 10mm or above) The armour wouldnt have the required csa nessacary
 
You cant export the earth on pme if there is water or gas services in the outbuilding unless you have permission from the energy supplier.
You would install a rod then bond from outbuilding consumer unit
Terminate exported cpc at garage end in plastic enclosure so that the two earthing systems are totally seperate
 
Yes technically you should first contact the DNO before exporting PME.
However in practice, it's a complete waste your time.
The DNO connot refuse to allow you to extend the PME, without good cause.
The DNO would be hard pressed to justify their refusal, if the work complies with BS7671.
 
You cant export the earth on pme if there is water or gas services in the outbuilding unless you have permission from the energy supplier.
You would install a rod then bond from outbuilding consumer unit
Terminate exported cpc at garage end in plastic enclosure so that the two earthing systems are totally seperate
Thats how I would do it, I hate the Idea of Extending TNT (PME) earthing outside..(makes me shiver when i see hot tubs on PME) but thats just me because ive seen lost neutrals before!! not nice seeing the whole instalation live compared to the mud outside!
but this arguments been done to death.. as its been mentioned there is a sticky thread somewhere on this
 
Last edited by a moderator:
Thats how I would do it, I hate the Idea of Extending TNT (PME) earthing outside..(makes me shiver when i see hot tubs on PME) but thats just me because ive seen lost neutrals before!! not nice seeing the whole instalation live compared to the mud outside!
but this arguments been done to death.. as its been mentioned there is a sticky thread somewhere on this

You must be one of the very, very few that has!! lol!!!
 
nowt wrong with exporting PME....of course there are certain things...such as hottubs....that you would rod....but come on....whats this thing about exporting a good, reliable earthing arrangement where low impedences are easily acheaved..?...
 
wouldn't use the armour for the cpc or main bonding conductor. would use either separate 10mm main bonding conductor or use the cpc (3rd core of the swa if 10mm or above) The armour wouldn't have the required csa necessary

I would have absolutely No Problem with using the SWA as my CPC and a 3rd core (10mm and over) as my bonding conductor. SWA CSA will generally comply with CPC requirements up to 95mm in both PVC/XLPE insulated cables (unless of excessive length) from 2 core to 4 core configured cables.

Another point to consider, ...when taking a bonding conductor to an outbuilding or whatever, you are effectively ''Extending'' the equipotential zone, NOT Exporting it!!
 
You must be one of the very, very few that has!! lol!!!
Im sure we have had this conversation before!! :) and as i said before.. it only takes one lost neutral to kill someone.. stepping out the hot tub! i would prefer a crappy stake and a tingle if there was a fault, than 230v going up me leg!! I prefer the fact that it would take a few faults to ocour to get a dangrous touch voltage with a TT than the single fault with exported PME.. but thats my EXPERIANCE when ive seen flexy hoses blown out under sinks etc :) but as previously stated its been argued before :)
 
Im sure we have had this conversation before!! :) and as i said before.. it only takes one lost neutral to kill someone.. stepping out the hot tub! i would prefer a crappy stake and a tingle if there was a fault, than 230v going up me leg!! I prefer the fact that it would take a few faults to ocour to get a dangrous touch voltage with a TT than the single fault with exported PME.. but thats my EXPERIANCE when ive seen flexy hoses blown out under sinks etc :) but as previously stated its been argued before :)
well you could always quickly withdraw said leg back into hottub....there! Problem solved!....
 
if you were using swa 3core 10mm or above wouldnt the 3rd core be used as a combined cpc/bonding conductor ??

i also agree the armour could be used as either cpc or bonding conductor if csa is adaquate, i just prefer to use the extra core or a seperate bonding conductor.

totally agree with your point re extending the equipotential zone if you provide a suitblly sized bonding conductor back to MET.

the number of people who just want to bang in a rod and replace a low resistance earth path with a relatively high resistance rod when not needed is staggering. the actual circumstances of the installation dont seem to be beeing assessed. just because its PME doesnt mean it has to be TT at the outbuilding. Exporting a pme supply under the right circumstances is not dangerous, extending the equipotential zone via bonding conductor is not dangerous, you just have to assess the installation and use your common sense and knowledge as to which earthing arrangement is required.
 
i just dont agree with people stating that exporting/extending pme is dangerous or not allowed. the hot tub example shows each installation must be assessed, and the earthing arrangement selected accordingly. As long as the main equipotential zone is extended to include the outbuiding/garage/shed in the event of a lost neutral a dangerous potential should not arrise. surely that the whole point of extending the equipotential zone to include the outbuilding
 
Last edited:
Im sure we have had this conversation before!! :) and as i said before.. it only takes one lost neutral to kill someone.. stepping out the hot tub! i would prefer a crappy stake and a tingle if there was a fault, than 230v going up me leg!! I prefer the fact that it would take a few faults to ocour to get a dangrous touch voltage with a TT than the single fault with exported PME.. but thats my EXPERIANCE when ive seen flexy hoses blown out under sinks etc :) but as previously stated its been argued before :)

was said hot tub effectively bonded back to the MET ? (equipotential zone extended) or had the pme earth just been exported. Just wondered big difference between exporting/extending zone.

for this installation a local earth rod, inrelation to the hot tub would make perfect sense. especially if the hot tub was located on open ground.
 
Last edited:
The hot tub Was an example :) Ive exported PME to out buildings and have no problems doing so,, as long as the risks are known. But having seen the mess that can be caused by a lost neutral, im just a little wary.As said above a PME supply to a hot tub with an external stake makes good sence. BUT how many people have installed hot tubs without the extra safty feature? oh and remember the RCD wont save you as it wont be unbalanced
PME is a good CHEAP for the DNO earthing system, but people should know the risks. long live TNS :)
 
Last edited by a moderator:
i agree tncs does have it problems but how many times does the dno loose the nuetral?? i guess its a case of making sure in the event of a lost neutral the ground and any extrenuous conductive parts are kept at the same potential to limit the risk of electric shock. this can be acheived by effective bonding or by using a seperate earth rod. in my expieirence with pme it comes down to weather it is more cost effective to install a earth electrode or extend the main bonding. if thers no extrenuous conductive parts then just export the earth as you would with a tns system.
 
When you think about it, Hot Tubs and jacuzzis would be standing on a wooden decking, or a concrete base with a wooden decking surround and with steps. You would be mad to locate one of these units on bare ground, i've certainly never seen one. All these units have the tub's made from a glass fibre, any earthing on the unit is limited the pump and heating plant, even the pipework is all PVC, even if permanently piped in.

The chances of taking a belt in such circumstances, is pretty remote, about as remote as kids playing with a hose pipe or plastic paddling pool on hot steamy days in the back garden!! Though i can't see why you shouldn't take the extra precaution of staking the the tub installation....
 
Your just keeping the potential equal to the surrounding ground potential. Personally i would only consider using a rod where the supply is PME/TNC-S. Isolating the supply PME earth before connection to the Tub's plant supply, and replacing with the electrode's earth. You will obviously need to make sure there is suitable RCD protection, but that is normally covered in the tub's electrical system, by the manufacture. I've haven't seen one that hasn't been integrally RCD protected for years now!!

I can't honestly say i've ever rodded a Hot Tub or Jacuzzi professionally. Never rodded any i've done privately for friends etc either, of which there have been plenty in Cyprus. But then there is no domestic PME/TNC-S in Cyprus... lol!!
 
Ah right I thought you meant rodding at the jacuzzi as well as being connected to the PME supply.
You know having both at the same time.

The subject of earth rods is really interesting you said that in the fifties all council houses had rods fitted as well as being connected to a TN-S earthing system.

What would be the point of rodding if you were already connected to a cable with an EFLI of 0.8 Ohms or lower?

I've also heard it said that it is good to rod at the consumers installation if they have PME so that PME and a rod are both used together at the same time, I am just trying to figure out why.

Why would you want an earth rod and PME both fitted together in the same earthing system?

Thanks.
 
Last edited:
Fitting an earth rod at origin of the installations supply on a PME supply is like adding another rod to the Multiple Earths of the PME supply, better to know that the first rod is close to your installation rather than up the road a piece!! lol!! Just make it a good rod though, a standard UK 200 ohm rod will be next to useless!!!

As for the the old council habit of installing a small earth plate or rod to TN-S supplied houses etc, no idea the thinking behind it, but can't see any down side to it either...lol!!!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
seperate bonding conductor
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
34
Unsolved
--

Advert

Thread statistics

Created
ianphilip007,
Last reply from
Engineer54,
Replies
34
Views
4,547

Advert

Back
Top