Seperate EICs | on ElectriciansForums
Discuss Seperate EICs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Daveyboy
Hi guys, If in a house you changed a consumer unit and fitted 3 new circuits.
would you use 1 eic or seperate eics for each circuit? I keep getting conflicting views
With the elecsa certs it has the max zs permitted by bs7671 do you put down the figures as in bs7671 or use the 0.8x rule? Thanks
As in bs7671....because that is the maximum permissible Zs....Confusing though,because if any circuits exceeded the 80% rule of thumb you would possibly have to do something about it.
Reply to Seperate EICs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thanks for the advice, I actually had no idea about the HMO licensing rules so have learnt a lot. Just did a search, its not licensed as an HMO...
With all due respect, if you're in a position, trained and skilled to be undertaking these works, you should really know this stuff. Especially as...