Is 0.06 ohms the max zs?
Did 300mm give you an R1+R2 of 0.04 ohms?
Could you post the cable calc for the two options. IMO an external Cpc would be electrically preferential but I guess the brains at IET think otherwise.
I think there is a bit of confusion here, the thing I was trying to highlight was that the software said it was ok to use a 5c cable with an integral earth conductor, but not ok to use a 4c cable with a supplementary earth of the same size.
I have been thinking about this and and the only thing that comes to mind is the programme assuming the cpc will pass through a separate hole to the line conductors which would not happen if it were a core of the cable which may under fault conditions be problematic, maybe.
Reply to Seperate / Integral earth CPC on 400A supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
It's the same with any system, if you put poo in, you get poo out!