A bit like Boydy says. For me the key difference between initial verification and periodic inspection (EICR) for the testing sequence is that on initial verification you have to do the testing in a set sequence to prove its safe to put power on (e.g. continuity of conductors/bonding, IR, polarity etc....)
On a periodic the system has already been powered up and is relatively safe (so to speak!) so you the testing sequence is far less important. The inspection bit to prove to yourself its safe to test now becomes more important than the actual testing sequence!
On a periodic the system has already been powered up and is relatively safe (so to speak!) so you the testing sequence is far less important. The inspection bit to prove to yourself its safe to test now becomes more important than the actual testing sequence!