setting a dol starter thermal overload | on ElectriciansForums
Discuss setting a dol starter thermal overload in the Australia area at ElectriciansForums.net
W
Welchyboy
as in the title can anyone help with selecting and setting the limit on a thermal overload relay, the motor is rated at 2.2 KW single phase, is it a case of run the motor at full load, clamp measure the max A then set the overload just above, or set the overload to just below the max CC Capacity of the supply cable?
thanks
If the motor load is fairly constant like a fan unit I measure the run current then add 5% and set the thermal at that.
I would always make sure the overload setting doesn't exceed the max run current on the motor plate. Even at 5% over the max run current you probably won't burn the windings but the excessive heat degrades the bearing lubricant and shortens the life of the motor considerably. This is especially true with the cheaper Far East imports.
Twenty or thirty years ago there was a built-in safety margin and you could run a motor over its specified current with no noticeable consequences......but.....alas.... those days are long gone
Excelent post Marvo
Reply to setting a dol starter thermal overload in the Australia area at ElectriciansForums.net