Joined
Mar 27, 2014
Messages
197
Reaction score
38
Location
Stirling
Hi all can anyone give me there thoughts on setting of thermal overloads. I have heard all types such as set them at 110% of FLA. Set them 125% of FLA. Set them at 100% of FLA. Get running current and set them 10% above this. But I have heard a lot set them at 110% to avoid nuse tripping?

Thanks trig
 
Set standard motor controler thermal overloads at 100% FLA, not at 110 or 125%!! Just think about what you are doing by setting the thermal protection of a motor.....
 
Set standard motor controler thermal overloads at 100% FLA, not at 110 or 125%!! Just think about what you are doing by setting the thermal protection of a motor.....
Hi there thanks for replying. I was just wondering why so many people I speak to set them at 110%. Why are they setting them higher than 100% ?

thanks
 
Hi there thanks for replying. I was just wondering why so many people I speak to set them at 110%. Why are they setting them higher than 100% ?

thanks

Because most of those have little to no working knowledge of motor protection. I've even heard of college lecturers coming out with this sort of crap, which to me just goes to show the standard of some of these college lecturers today. let alone some of the scaremongering views many persist in perpetuating!!

Those 110/125% etc of FLC, stem from the era of the old oil filled dash pot overloads, they have long since disappeared, no compensation is now necessary on the modern motor overload modules of today....
 
Last edited by a moderator:
As expressed already by E54....set to FLC of motor, if you are experienced in this area then lower than FLC may be set up by knowing the running current demand of the motor - this can be used as an early warning indicator of issues like worn bearings etc etc which can be rectified immediately by changing O/L to FLC and programming a shutdown service in when more convenient.
 
Those 110/125% etc of FLC, stem from the era of the old oil filled dash pot overloads, they have long since disappeared, no compensation is now necessary on the modern motor overload modules of today....

They’re still out there. Most will have a plate stating the setting level. For cane duty they also provide S/C protection. Cranes are a special case where the motors are dual rated for short term and continuous running.

Thermal O/L’s set at 100%
 
They’re still out there. Most will have a plate stating the setting level. For cane duty they also provide S/C protection. Cranes are a special case where the motors are dual rated for short term and continuous running.

Thermal O/L’s set at 100%

Let's hope these old dash pot contactors are being maintained then. But i'm sure you're right in that there still lurking around and still filling a function, although i haven't personally seen any of them around for now for literary donkeys years....
 
They’re still out there. Most will have a plate stating the setting level. For cane duty they also provide S/C protection. Cranes are a special case where the motors are dual rated for short term and continuous running.

Thermal O/L’s set at 100%

I've only ever seen them on fuses tony, never knew they used Thermals OL'S
 
No joking Geordie, I have worked on a steam crane. It’s now at Rutland railway museum along with two of our loco’s.
I’ve got some pictures of it, I’ll send them to you later.
 

Reply to Setting thermal overloads three phase direct on line motor in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
289
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
792
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
822

Similar threads

Hello, Last year my 30 year old Static Pase convertor stopped working, the 3 phase motor is 0.55KW / 0.74HP and drives a small lathe. When I...
Replies
0
Views
189
https://sravivarman.com/technical-articles/parallel-operation-of-thyristors/ Series resistor, or bigger series resistor, needed?
Replies
1
Views
152

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top