Can someone please tell me the maximum Zs for a 10A Type C Rcbo to BS En 61009-1?
where's 200 ohms come from?Lol,
The MCB part of it from 41.3 gives 2.3 Ohms
The RCD part of it from 41.5 gives 1.67k Ohms, which translates into 200 Ohms
Looks like you're both right
However, .............. we always look at a R1 + R2 + the Suppliers Ze for a TN system which would satisfy the disconnection times in 41.1
where's 200 ohms come from?
where did 200 Ohms come from?
Thanks for the replies guys. I was under the impression table 41.5 was for a TT system and 41.3 for a TN system.
if max zs = 1667 we are still limited by the l-n impedance of the circuit where a 5s disconection time is required
where's 200 ohms come from?