Hi all
I have a situation that I can't get my head around and hoping someone can help!
A client reported receiving shocks from her shower. When I visited the property, and when wet if you touched the metal parts of the shower (which was not electric), and the bath taps at the same time you got quite a shock from it.
There was no earthing system installed to the property. Nor was there water bonding or gas bonding.
They didn't want to get a TNCS system installed despite my recommendations, and asked me to install an earth rod which I did (ze 109 ohms). I also installed gas and water bonding. RCD protection to all circuits.
However, we still experienced the shock even with the earthing installed.
I did a bit of fault finding and turns out an 'unknown' circuit on a 6a MCB was causing the problem. When I disconnected the circuit, no more shocks from the shower/taps.
I thought installing an earth rod and water bonding would have stopped the shocks - am I wrong?
Grateful for any input. Kelly x
I have a situation that I can't get my head around and hoping someone can help!
A client reported receiving shocks from her shower. When I visited the property, and when wet if you touched the metal parts of the shower (which was not electric), and the bath taps at the same time you got quite a shock from it.
There was no earthing system installed to the property. Nor was there water bonding or gas bonding.
They didn't want to get a TNCS system installed despite my recommendations, and asked me to install an earth rod which I did (ze 109 ohms). I also installed gas and water bonding. RCD protection to all circuits.
However, we still experienced the shock even with the earthing installed.
I did a bit of fault finding and turns out an 'unknown' circuit on a 6a MCB was causing the problem. When I disconnected the circuit, no more shocks from the shower/taps.
I thought installing an earth rod and water bonding would have stopped the shocks - am I wrong?
Grateful for any input. Kelly x