I was hoping someone can help me, as I'm stepping out my normal line of work to help a friend.
I'm an electrical fault finder on the railway, but previously did some industrial work and so have BS 2391.
My friend is installing a small kitchen in a shop, the shop fitter has handed him some paper with the following circuits for the cookers, extractor fan and fridges, as follows:
A/ 3KW (Cooker/Grill)
B/ 3KW (Heating area)
C/ 5KW (Cooker/Grill)
D/ 13A Spur 1KW (extractor fan)

There is already a ring main for the fridges.

So my question is- I believe the A/B/C/ can run off a 45A breaker with 10mm cable (run of 5m), which feeds a double pole isolating switch, but is it ok to feed three items off of one isolating switch? I thought there might be a limit of two?
And does the fitter intend to take the spur for D/ off of this one isolator also?

While I am in the electrical field, I don't have much experience with thiese sorts of installations so couldn't really explain it to my friend, so really appreciate any help you can offer.
 
you could take D as a spur from the ring. as for A/B/C i would run a separate radial for each, each with it's own isolator.
you can then use 4mm or 6mm for each.
 
As Tel says mate, but you will need RCD protection. I would do as tel says, but fit a seperate consumer unit with RCBO's for each circuit, this is not the cheapest solution, but if you fitted a RCD protected CU you would loose all circuits if you had a fault, the RCBO route would just trip the offending circuit.

Cheers...........Howard
 
The 3 KW heating radial could be run in 2.5mm with a 20 amp mcb if prefered and a double pole switch if its a fixed load

Another method of wiring this area is as found in ready made chip shop ranges
A seperate consumer unit fed by a sub main with circuits local to the loads
It may be more adaptable for any alterations to the cooking area,adding display lighting etc
 

Reply to Shop Kitchen Supplies Installation Query in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top