Short between N-cpc of another circuit? | on ElectriciansForums

Discuss Short between N-cpc of another circuit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

F

Flakey

I have a lighting circuit on one RCD and ring on other RCD I'm getting neutral of ring to earth of lighting circuit fault. But clear IR between Neutral of ring and cpc of ring as far as I know the circuits are and should be electrically separated. All cables tested are tested out of terminal bars as neutral and earth are connected on the intake. Any ideas appreciated. All I can think is maybe a nail between two cables I.e lighting circuit and ring

Cheers
 
Last edited by a moderator:
I initially did test on each circuit 1 at a time and there were no faults to the individual circuits. Only when i powered up the the board first RCD with lighting stays on second RCD with ring tripped when Lightin circuit MCB is switched on. Initially thought was a case of crossed neutrals in the board which has turned out not to be the case. So IR test between all of the ring cables and earth bar identified Lighting cpc as culprit pulled cpc from earth bar and pulled neutral of ring tested between them dead short. I mean all i can think at this point is a screw or something similar may have gone through grouped cables skinning the cpc in one cable and neutral in the other thus creating a dead short. But i want to make sure im not over thinking before i start cutting through newly painted walls :). will be breaking the circuits down tommorow as i had a painter in the apartment today wanting light.

Thanks again for any help

Cheers!!
 
Tbh im on day rate but its one of those were you want to get to the bottom of the problem with as little destroying as possible lol!!
 
then you first need to split the RFC down to find which section has the fault. then get the hammer out.
 
Did you run the cables?, do you know the runs, I would bet it's going to be on route to cu the finals where they are bunched together, or somewhere where the 2 cables are running together.
 
You need to elaborate on the phrase "dead short". Is this 0.00 Meg, on an IR setting, or some very low Ohm reading on continuity?

If there is a nail or something connecting CPC of one to N of another cable, then you should be able to measure the resistance in Ohms, likely some fraction of an Ohm. You might well be able to use this reading to estimate how far along the cable run the fault is, remembering of course the different CSAs of the two cables.
 

Reply to Short between N-cpc of another circuit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
314
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
836
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
948

Similar threads

Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
383
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top