I've come across a fault at work. Fuse keeps blowing when they put it in. I haven't tested for a while, and so am pretty sure I'm missing some basic steps with the fault finding process.
Small room. 1 emergency fluorescent light fitting, 1 bulkhead emergency fitting.
Fluorescent is plugged into a click on the ceiling. Live and Neutral have been wired from this click.
Dead shot L-E.
Unplugged click. d/c bulkhead. Fault clear.
IR test on disconnected cables at bulkhead - >999.
As soon as I connect either fitting, dead short L-E.
What am I missing?!?!
I'm ready for all the abuse.... Come at me... ;)
 
It would point to incorrectly wired click unit IE Live is in the earth terminal etc or the click is internally faulty and the physical action of plugging into it creates the fault... this is going only on the info' you provided, if you have missed any tests or have not been forthwith with all the information then we may be going down the wrong path with my suggestion.
 
I've come across a fault at work. Fuse keeps blowing when they put it in. I haven't tested for a while, and so am pretty sure I'm missing some basic steps with the fault finding process.
Small room. 1 emergency fluorescent light fitting, 1 bulkhead emergency fitting.
Fluorescent is plugged into a click on the ceiling. Live and Neutral have been wired from this click.
Dead shot L-E.
Unplugged click. d/c bulkhead. Fault clear.
IR test on disconnected cables at bulkhead - >999.
As soon as I connect either fitting, dead short L-E.
What am I missing?!?!
I'm ready for all the abuse.... Come at me... ;)
Been doing the bang test a few times then? sounds as though the EM fittings have developed a fault possibly by subjecting them to being re-energised under faut conditions, maybe? Is this a new installation? if yes could be you have the klick plugs wired up wrong.
 
Existing installation. I haven't put the fuse back in personally, but that's not to say somebody hasn't tried before me. When I d/c the L&N that goes from the click to the bulkhead the fault cleared. It all points towards the bulkhead. Funny, because they I had a carbon copy of this fault a few weeks back, and the only way the fault cleared was when I d/c the neutral going from an existing fitting to a new bulkhead. They've basically borrowed neutrals from existing fittings and what not to get these bulkhead light fittings on. All seems a bit heath robinson to me.
 

Reply to Short Circuit When Emergency Lights Are Connected in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
760
  • Question
Or a combined fitting in each row.
Replies
19
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top