The resistance would have to be 1 ohm for a current of 230A
The earth fault loop impedance at the supply terminals for a new PME supply will typically be below 0.35 ohm.
At 0.35ohm you get a fault current of 657A
At a possible (and pretty realistic) 0.1 ohm the fault current would be 2300A
If the installation is very near to the substation then the fault current can be even higher.
The DNO will usually state a maximum prospective fault current of 16kA for a single phase supply as this is the upper limit they usually work to when designing supplies.
But you also need to consider that 230V is a myth which only exists in the textbooks, in actual fact the substation will be fixed at an output of 250V so the fault currents will be a little higher than that.
Also consider that the fault current could be a short circuit rather than an earth fault, so the potential could be theoretically 400V (433V in reality) if it is a three phase supply