Should internal links in consumer units be double insulated where TT earthing is present | on ElectriciansForums

Discuss Should internal links in consumer units be double insulated where TT earthing is present in the UK Electrical Forum area at ElectriciansForums.net

spud1

-
Arms
Joined
Oct 23, 2010
Messages
354
Reaction score
54
Location
Somerset
Hi,

So I was reading the notes on regulation 531.3.5.3.2.201 (Page 156) today and noticed Note 1 that consideration should be given (Where TT earthing is present) to the manufacturer's internal line cable links on the supply side of an RCD being insulated AND sheathed! Does anyone know of any distribution equipment manufacturer that either fits double insulated cable links as standard or offers an alternative double insulated kit of leads?

Cheers
 
Taken from Hager’s CU instructions

TNC-S, TN-S when installed in an electrical installation complying with BS 7671
Hager recommends for TT systems a 100A type S time delayed RCCB or a main switch with RCBO protection only on all outgoing circuits.
 
Last edited:
Taken from Hager’s CU instructions

TNC-S, TN-S when installed in an electrical installation complying with BS 7671
Hager recommends for TT systems a 100A type S time delayed RCCB or a main switch with RCBO protection only on all outgoing circuits.
They are wrong if they are recommending an RCD main switch with SP RCBO's. A fault on a final circuit will not disconnect the neutral and probably take out the main switch as well
 
They are wrong if they are recommending an RCD main switch with SP RCBO's. A fault on a final circuit will not disconnect the neutral and probably take out the main switch as well
No it’s a main switch with rcbo’s or dual rccb’s with an S type upfront is what they mean, ( I think).
Not very clear but that would make more sense.
[ElectriciansForums.net] Should internal links in consumer units be double insulated where TT earthing is present
 
Hi,

So I was reading the notes on regulation 531.3.5.3.2.201 (Page 156) today and noticed Note 1 that consideration should be given (Where TT earthing is present) to the manufacturer's internal line cable links on the supply side of an RCD being insulated AND sheathed! Does anyone know of any distribution equipment manufacturer that either fits double insulated cable links as standard or offers an alternative double insulated kit of leads?

Cheers
They aren't double insulated they are insulated and Mech protected, never seen a cable with the double insulation marked on it.
 
They are wrong if they are recommending an RCD main switch with SP RCBO's. A fault on a final circuit will not disconnect the neutral and probably take out the main switch as well
There is no requirement for a protective device to isolate the neutral under fault conditions, regardless of earthing system type.
 
There is no requirement for a protective device to isolate the neutral under fault conditions, regardless of earthing system type.
I think radiohead's point is if a final circuit has a N-E fault then you will probably trip the incomer RCD as the SP RCBO will trip but not isolate the neutral fault.

So it is not necessary according to the regs as such, but it is far better to have a N-switching RCBO if you can. I guess it indirectly comes under the requirement for selectivity, etc (off hand don't remember the numbers).

Not that many do unfortunately, but at my last count Wylex/Crabreee/Fusebox (the miniature version) RCBO for consumer DB do switch neutral.
 
There is no requirement for a protective device to isolate the neutral under fault conditions, regardless of earthing system type.
You miss the point. The requirement is that a single fault on a final circuit does not disconnect the entire installation. If there is an RCD main switch failure to disconnect the N on a faulty final circuit will probably disconnect the entire installation. Because of an indirect consequence of a single fault it is in effect a requirement that where an RCD main switch is used with RCBO's then each RCBO must disconnect both poles.
edit...post crossed with PC1966
 
Back to the OP's point - I really think that any properly installed metal CU is going to be fine.

I.e. where the tails are double-sheathed as expected, they enter by a proper gland for support and protection from damage, and the CU has been installed with care to make sure the busbar is in place and clamped correctly, etc.

Obviously all circuits have to be RCD protected as TT rarely will have a Zs able to disconnect a MCB, and at that point I would state my personal preference for both an up-front 100mA/300mA delay RCD and then whatever 30mA instant RCD/RCBO are needed for "additional protection".

In my case it is less about the risk of an internal CU short, than about the risk of a 30mA RCD failing to trip and so the earth/CPC remains live for a prolonged period. With an incomer RCD there is no single point of failure.
 
Last edited:
You miss the point. The requirement is that a single fault on a final circuit does not disconnect the entire installation. If there is an RCD main switch failure to disconnect the N on a faulty final circuit will probably disconnect the entire installation. Because of an indirect consequence of a single fault it is in effect a requirement that where an RCD main switch is used with RCBO's then each RCBO must disconnect both poles.
edit...post crossed with PC1966

When were Wylex/Crabtree SP&SN RCBO's first introduce? I have a feeling that many TT installs have been none compliant since July 2015, if that's the case.
 

Reply to Should internal links in consumer units be double insulated where TT earthing is present in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
770

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top