Hi guys.
Im moving a consumer unit for my brother and where I was going to run a 25mm armoured through the building he has decided to put a window directly above the cut out.
After explaining to him the only way I could do it would be to put a piece of earthed metal trunking on the inside (red line on photo) and bring a stud wall out 50mm, he's not happy with this as the wall would stick out too much to cover the trunking. After my advice, he has asked his friend what he would do and he said he wouldn't use the trunking and just clip direct to the wall??? Surely this isn't good practice with an incoming supply especially with it being tails?
What do you think?
Im moving a consumer unit for my brother and where I was going to run a 25mm armoured through the building he has decided to put a window directly above the cut out.
After explaining to him the only way I could do it would be to put a piece of earthed metal trunking on the inside (red line on photo) and bring a stud wall out 50mm, he's not happy with this as the wall would stick out too much to cover the trunking. After my advice, he has asked his friend what he would do and he said he wouldn't use the trunking and just clip direct to the wall??? Surely this isn't good practice with an incoming supply especially with it being tails?