Shower and cooker circuits shown as 2.5mm2 on shedule but overall condition satisfactory | on ElectriciansForums

Discuss Shower and cooker circuits shown as 2.5mm2 on shedule but overall condition satisfactory in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

UKMeterman

-
Arms
Joined
Feb 20, 2011
Messages
969
Reaction score
430
I am reviewing a EICR for a property I am buying. The vendor has had the EICR done, but both the Cooker and Shower are on 40A 60898 B curve mcbs and the cable type is shown as 2.5mm2 type A install methord C. I suspect a clerical error but as it is in the vendor document pack what would you suggest? The cooker is a four ring built in electric hob. The shower is an electricaly heated shower rateing of which to be checked tomorrow.
All the circuit insulation measurements are 500M ohm which is a bit sus.
 
Last edited:
I don't see the 500 Meg ohm as being 'suss' why wouldn't it have been assuming this is just a reading to earth.

I was guessing it seemed suss as >999 is the sort of reading a lot of people would expect when results are the same on all circuits. Stands to reason the tester measures a maximum of 500mΩ.
 
For an EICR I would question whether they really disconnected all connections across line and neutral to achieve an L to E reading.

From information provided by the OP, it looks as though the EICR raises a number of questions about exactly what 'testing' & 'inspection' took place.
 

Reply to Shower and cooker circuits shown as 2.5mm2 on shedule but overall condition satisfactory in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top