Hi Guys
Does a 9.5kw shower require 6mm cable or 10mm shower is approx 10 mtrs away from consumer unit most of the cable will be ran in the loft space, I know its border line but what would you guys use......thanks in advance.
 
I did exactly this earlier this week.
Cable calculations do allow 6mm clipped direct,i.e. with no insulation round the cable. But, I think insulation will be put on top of the cable in the future, so I erred on the side of caution, and put in 10mm. The price difference in the cable is minimal (for the 13m run I did, maybe ÂŁ7 difference), and it is future proof for a bigger shower, as well as ensuring it meets all the Regs if the loft get further insulation.

TBH, I cannot see why anyone would use 6mm for a new shower any more.

HTH
Alan.
 
Hi Guys
Does a 9.5kw shower require 6mm cable or 10mm

Well, that depends upon the installation method.
If the cable is installed 'clipped direct' (ie no insulation) then 6mm has a rating of 47A in BS7671.
As a 9.5kW shower pulls 39.6A then the load is well in.
As the load would be 'occasional' rather than 'continuous' you'd be okay on a 40A mcb.

I keep shower cable clear of insulation by mounting up on woodwork and where it passes through the insulation layer I use 4 inch soil pipe to maintain a large 'air gap' around the cable.
 
Just had the same conversation with a guy going for his DI assesment, he was told to put in 16mm for a 9.5kw, 10m run under floorboards. I did tell him to redo the calculations as I thought 16mm was overkill.
 
showe me a 9.5KW shower that draws 9.5KW and i'll start looking out the window for flying pigs. never seen a 9.5KW draw more than 32A. over rated by manufacturers to push sales. the old 7kw got you just as wet.
 

Reply to Shower cable size in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
933
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Better off with the click prw213 as it has twin screw termination.
Replies
9
Views
984
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
293

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top