shower cable | on ElectriciansForums

Discuss shower cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

B

beaver74

9kw shower to run on a 6.0 swa clipped direct for 30m
but for 2 metres it goes through a boiler rm so what is the min amount you guys whould take including a temparature factor in calculation
although these results are addiquite i will be running 10.0mm but am i being over the top
any thoughts
 
I think you would be wise to run a 10mm.

9000W / 230 = 39amps

Quick domestic cable circuit chart attached.
 
Last edited by a moderator:
9kw shower to run on a 6.0 swa clipped direct for 30m
but for 2 metres it goes through a boiler rm so what is the min amount you guys whould take including a temparature factor in calculation
although these results are addiquite i will be running 10.0mm but am i being over the top
any thoughts


Volt drop should also be taken into consideration as well as the correction factor for going through the boiler room.

Not knowing ambient temp in boiler room for correction factor it could be that by time these factors are taken into consideration you could be looking at 16mm.
 
Bear with me for this one.. My calculations are working out to be 6mm cable. I have noticed that my cable size is considerably smaller than your 10mm and 16mm, but have you noticed that it is SWA? swa can take a lot more current that standard t+e. Anyway my calcs are;

Ib = 9000/230 = 39.1Amps
In = 40 Amp
So It = In / Ca-Cg - Cc - Ci
= 40 / 0.91 (In / Ca) (Ca - calculated at 40 degrees c)
= 44 Amps
4mm cable swa can actually take this current, but fails on volt drop (14.1v) max is 11.5v.
Next cable size is 6mm and can take 62 Amp with volt drop of (9.26v) and is below the max 11.5v.
If it were me i would be putting in 6mm.
Comments are welcome and hope i havent made a wrong judgment - still in training so be kind!!!

Hope this helps anyway!
 
Bear with me for this one.. My calculations are working out to be 6mm cable. I have noticed that my cable size is considerably smaller than your 10mm and 16mm, but have you noticed that it is SWA? swa can take a lot more current that standard t+e. Anyway my calcs are;

Ib = 9000/230 = 39.1Amps
In = 40 Amp
So It = In / Ca-Cg - Cc - Ci
= 40 / 0.91 (In / Ca) (Ca - calculated at 40 degrees c)
= 44 Amps
4mm cable swa can actually take this current, but fails on volt drop (14.1v) max is 11.5v.
Next cable size is 6mm and can take 62 Amp with volt drop of (9.26v) and is below the max 11.5v.
If it were me i would be putting in 6mm.
Comments are welcome and hope i havent made a wrong judgment - still in training so be kind!!!

Hope this helps anyway!


hi all

are you going to use a 90 degree thermosetting armour cable as bolier rooms can reach some pretty horendous temps in the summer

also in training for 2391-20

also what protective device is being used ?

cheers
 
was not shore wether 70/90 deg swa but was really waiting to see if any one would bother making full allowance for just the 2m that cable will be subjected to any heat
 
was not shore wether 70/90 deg swa but was really waiting to see if any one would bother making full allowance for just the 2m that cable will be subjected to any heat

I think Dan is right. He has allowed for thermosetting swa with an ambient temperature of 40 degrees.

There is only 2 metres going through the boiler room and with the shower pulling less than 40 amps in cable able to carry over 60 amps this should not be a problem.

It's intresting to note however that under the 16th edition with 4% volt drop, 10mm cable would have to be used. One of the very few instances of the 17th saving money. Dont forget that circuits in rooms with baths or showers will need RCD protection
 

Reply to shower cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

Yes, that was actually something making me uncomfortable too, the bonding of it all. I need to have another look at it, I'm not sure if the...
Replies
2
Views
825

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top