Shower circuit (40a mcb 10mm cable 8.5kw shower ) tripping after 5 mins RESET trips after 2 mins...changed shower /cable /isolator still tripping I'm stumped
Discuss Shower circuit tripping in the UK Electrical Forum area at ElectriciansForums.net
Randomly replacing parts without knowing the cause is not the way forward and is costing money. What tests have you done?
Mcb on order only changed cable as easy swap and showed signs on damage and stripped to far back not long enough to re terminate.is there a way to test mcb is faulty?Cable change was probably not required
if the current is constantly below 40A then a faulty breaker is likely, assuming it is just an Mcb.
if it is an rcbo then of course there could be other root causes.
Reply to Shower circuit tripping in the UK Electrical Forum area at ElectriciansForums.net