Hi All,
I have a shower to install for a very difficult customer. When quoted for the job I stated as its only on 6mm cable so she has to get a shower of equal or less kw than the one being replaced. So what does she do? Buys a 9.5kw shower when I pointed out the wording on the quote she returned with the instruction book for the shower which had a table in it showing the cable size that can be used with it and it states 6mm fine if the run is under 26m and on a 40a mcb! If the manufaturer of the shower is stating its ok what chance have I got convincing her. I get a lot of work from this pain in the rear end so am trying not to get too stroppy with her as she just doesnt get it. What would you do in this situation?
I have a shower to install for a very difficult customer. When quoted for the job I stated as its only on 6mm cable so she has to get a shower of equal or less kw than the one being replaced. So what does she do? Buys a 9.5kw shower when I pointed out the wording on the quote she returned with the instruction book for the shower which had a table in it showing the cable size that can be used with it and it states 6mm fine if the run is under 26m and on a 40a mcb! If the manufaturer of the shower is stating its ok what chance have I got convincing her. I get a lot of work from this pain in the rear end so am trying not to get too stroppy with her as she just doesnt get it. What would you do in this situation?