Went to a job today as a follow on from another sparks on our firm. Was a "fishy smell" reported, and was advised that the cable was undersized.
Get there today and find a 6mm cable, 40a MCB and 9.5kw shower; and this in the isolater...
Now, the supply voltage is 242, the cable run goes from the board, up to the first floor in a piece of conduit in the wall (reference method A) which rates at 34a, and then up a void behind the shower, clipped direct (reference method which rates the cable at 47a.
Obviously the cable at the lowest part (bit going through conduit) is carrying 39.25a; which is greater than 34a, and they're sending me back to put a 10mm supply in tomorrow. My argument is that the damage to the cable has been caused by a loose neutral at the isolater and that although the cable is undersized, it's not massively bad and probably wouldn't cause a huge amount of issues if the shower was run normally.
Opinions please boys....
Get there today and find a 6mm cable, 40a MCB and 9.5kw shower; and this in the isolater...
Now, the supply voltage is 242, the cable run goes from the board, up to the first floor in a piece of conduit in the wall (reference method A) which rates at 34a, and then up a void behind the shower, clipped direct (reference method which rates the cable at 47a.
Obviously the cable at the lowest part (bit going through conduit) is carrying 39.25a; which is greater than 34a, and they're sending me back to put a 10mm supply in tomorrow. My argument is that the damage to the cable has been caused by a loose neutral at the isolater and that although the cable is undersized, it's not massively bad and probably wouldn't cause a huge amount of issues if the shower was run normally.