Went to a job today as a follow on from another sparks on our firm. Was a "fishy smell" reported, and was advised that the cable was undersized.

Get there today and find a 6mm cable, 40a MCB and 9.5kw shower; and this in the isolater...

[ElectriciansForums.net] Shower Issue


Now, the supply voltage is 242, the cable run goes from the board, up to the first floor in a piece of conduit in the wall (reference method A) which rates at 34a, and then up a void behind the shower, clipped direct (reference method which rates the cable at 47a.

Obviously the cable at the lowest part (bit going through conduit) is carrying 39.25a; which is greater than 34a, and they're sending me back to put a 10mm supply in tomorrow. My argument is that the damage to the cable has been caused by a loose neutral at the isolater and that although the cable is undersized, it's not massively bad and probably wouldn't cause a huge amount of issues if the shower was run normally.

Opinions please boys....
 
Burning is only on the neutral term, so defo down to a poor neutral termination. You've been told to replace, so you should. However, I doubt it draws its rated max load in use!

I'd just replace switch if it were me, the damage was caused by loose termination. They run for such a short time, in reality 6mm will never be a problem. There are plenty of 9.5kw showers on 32A MCB's.
 
Borderline, depending on applied derating, 6mm is good to 40A CCC before derating...depends how where it's run....putty they don't do 35A breakers ... bet it would hold!
 
I go with that Dave
 
I would say it might not be a loose neutral connection. The other possibility is the pull cord itself is at fault. I have replaced 4 GET 45amp pullcords in this last week. All looked identical to that in the picture. I do a lot of maintenance for an estate agent and the most of the calls I get are showers and 9/10 its the pullcord. Try a different make as well as insuring all terminations are tight.
 
As I wrote in the first post, I know that the problem is at the isolator.

What I want discussed is the cable suitability. The only part where it doesn't comply is the metre drop down to the CU. Would you leave the cable and mcb, downrare the mcb or just rewire.

Highly likely I'll have to rewire tomorrow but I just think it's unnecessary.
 
Will a 10mm twin fit up the conduit? They are quite large by twin and earth standards. I've changed them too in the past, I think it doesn't help that they get twisted all over the show to get them to fit back if someone has fitted a box that's too shallow and it loosens the connections slightly
 

Reply to Shower Issue in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
813

Similar threads

Yes, that was actually something making me uncomfortable too, the bonding of it all. I need to have another look at it, I'm not sure if the...
Replies
2
Views
824

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top