I was called into a property where I was told that the shower fuse had blown. On investigation it turned out that a 9.8 KW shower was connected with 10mm T+E but only as far as the nearest fused spur on the upstairs ring main. They'd used a 45A cooker switch to terminate the 10mm then switched to 2.5 to connect into the supply side of the fused spur (which is powering a kind of sit down jacuzzi and seems to be correctly installed). They'd even done it in the old colours!

Apparently this work was done last August - I've taken photos - the 2.5 in the old colours was melted and fused together - it blew the RCD at the consumer unit and the tenants just haven't touched the shower since it started smoking.

1) What chance is there that the shower unit is still functional - should I tell her that she needs that swapping and will need a plumber?

2) What recourse does she have against the shower installers?
 
At least it blew the MCB/RCD. Just returned from a callout where the shower stopped working due to a broken isolation switch. Went to turn off the supply in the main consumer unit and couldn't find the shower fuse. Therefore turned off the 100amp main switch and guess what, the shower isolation switch still had 240v on the supply side. Undone the consumer unit cover and found the 6mm shower supply cable had been piggy backed off the incoming meter tails and no inline RCD. The only protection for the shower was the DNO fuse. Apparently the shower was installed by a plumber last year and he got an "electrician" in to connect the wiring, no certificates as usual. How do these people sleep at night ?
 

Reply to Shower lash up in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top