I was called into a property where I was told that the shower fuse had blown. On investigation it turned out that a 9.8 KW shower was connected with 10mm T+E but only as far as the nearest fused spur on the upstairs ring main. They'd used a 45A cooker switch to terminate the 10mm then switched to 2.5 to connect into the supply side of the fused spur (which is powering a kind of sit down jacuzzi and seems to be correctly installed). They'd even done it in the old colours!
Apparently this work was done last August - I've taken photos - the 2.5 in the old colours was melted and fused together - it blew the RCD at the consumer unit and the tenants just haven't touched the shower since it started smoking.
1) What chance is there that the shower unit is still functional - should I tell her that she needs that swapping and will need a plumber?
2) What recourse does she have against the shower installers?
Apparently this work was done last August - I've taken photos - the 2.5 in the old colours was melted and fused together - it blew the RCD at the consumer unit and the tenants just haven't touched the shower since it started smoking.
1) What chance is there that the shower unit is still functional - should I tell her that she needs that swapping and will need a plumber?
2) What recourse does she have against the shower installers?