i was asked to pull in a shower cable and leave in wall for future as customer has been roked into other work, so makes sense now as they have the room.

9.5kw shower on 6mm is fine according to osg upto 43m on ref method c. i only have an 8m run and is in rafters with kingspan but kingspan wont be touching it. it has 150mm rafter with only 100mm kingspan..
so at least a 50mm gap around cable
i said its dead on for 8.5kw shower but i do think 9,5 will be fine aswell.


thoughts
 
well righard there is only a 2.5mm in the 6mm t&E
If the cable is not in or under any insulation then 6mm should be OK for 9.5kW.
I get 3.88 with the adiabatic equation (for a 40A BS60898).

- - - Updated - - -

200 x 200 for the 40A breaker
How do you get that without knowing the PFC of the circuit? :bucktooth:
 
Richard has used the Ia value for the breaker (200A) which would cause the breaker to operate in 0.1secs.

S = √(I² x t) ÷ k
S = √(200² x 0.1) ÷ 115 = 0.55

However the correct value to use is the actual fault current that could flow in the event of a fault (Ipf = Uo ÷ Zs) which could be a lot higher if the Zs is low enough.
 
Last edited by a moderator:

Reply to shower on 6mm for future in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top