deano12929

Hi all

I am new to this so please be patient with me..

I have a 10.5 kw Shower with a supply of 230 v The power triangle equates that a 45.65 A protection is required.
The shower is wired in 10mm t&e approx 10 meters from the cu.

The problem i have is that the volex board i have only has 50A mcb's available for it.

The question is would that be ok or would i need to be nearer the 45A That is required.

Thanks

Deano

One who asks a question is a fool for five minutes; one who does not ask a question remains a fool forever


 
Hi all

I am new to this so please be patient with me..

I have a 10.5 kw Shower with a supply of 230 v The power triangle equates that a 45.65 A protection is required.
The shower is wired in 10mm t&e approx 10 meters from the cu.

The problem i have is that the volex board i have only has 50A mcb's available for it.

The question is would that be ok or would i need to be nearer the 45A That is required.

Thanks

Deano

One who asks a question is a fool for five minutes; one who does not ask a question remains a fool forever
Hi mate, yeah 50 amp would be fine its the closest to your 45 available;)
 
dont forget the overcurrent device is there to protect the cable (amongst other things)
50amp isnt a million miles away from the max for the cable...
personaly i'd go for a 32amp overcurrent device.
 
There's no diversity allowable on showers though, every shower i've done of that size has been put on 50 amp breaker and either 10 or 16 mm cable, i see what your saying though a 32 amp breaker does'nt reach that current for a while so unless you spends hours in the shower i doubt it would ever trip, just me i like everything to be right on paper;)
 
The calcs may show a load current of around 45 amps, but if you clamp an ammeter around the cable it's surprising how much less it often is. More like 38 to 40 amps so yes a 32 amp mcb will hold out until your bits have wrinkled up in the shower before tripping :D
 

Reply to shower protection help. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
935

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top