sparked out

A friends shower switch burnt out due to loose connection the problem is its a 10.5KW shower 40A wylex fuse and 6mmTE. Would the 6mm be ok with a 32A fuse and RCD, he does not want carpets lifting to run in a new 10mmTE
 
Well you could try that, but unfortunately the demand of the shower is 45.7 Amps so a 10mm cable (& RCD etc) is your (& his) only option.

P.s. That is probably why the cable is burning out ~ another reason not to have fuses within a domestic situation.
 
Last edited:
Replace the switch and then replace the shower with a 8.5kw shower! Cheapest option.

Replace the switch and run in 10mm supply cable! Dearest option.

You would need to inform the customer that he would really need to supply the shower through an RCD.

Cheers
 
I think it safe to say it would be good practice to advise a 10 mm cable for a new shower circuit as standard because it is likely at some point the customer will call a plumber or someone else to upgrade the shower.

Thus it could be acceptable that it is likely that the load could be increased in the lifetime of that cable. i.e. reg:132.3 NATURE OF DEMAND: Loads to be expected on the various circuits. also reg: 132.7 nature of location.

just my thoughts but please correct me if I'm wrong.
 
Last edited by a moderator:

Reply to Shower query in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
316
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
964

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top