mystic_carp
Hi, I was asked to look at fault today were shocks were being recieved whilst someone was using a shower. It did not occur constantly but when i was there I could find voltage between Earth and the screen this voltage went from 50v upto 150v gradually as the shower was switched on. there was also continuity between the earth when seperated from the appliance and the screen.(the screen is not bonded) I/R showed >299 between all conductors and cpc. I took the screws out of the frame but continuity still existed. But once I but back all equipemnt and turned on to see if still there the volts had gone. this fault seems to go and come back! I have bonded this to the earthed water pipe as when i got there linking the screen to the pipe tripped the rcd.
Does anyone have any thoughts as I would be gratful for any input
regards.
Does anyone have any thoughts as I would be gratful for any input
regards.