J

jodie

hi to all, i have just registered and very new so please be gentle with me!!
just a general querry my shower has started tripping out when in use but when i wiggle the ceiling pull cord about it comes back on been going on for about 3 wks now and tripping more and more only coming back on now for few seconds at a time compared to going off once when it started happening, i am getting anxious when my children are using it so think i need an eletrician.however i am scared about being ripped off as i know nothing on what to expect price wise... have been left in a mess beginig of year when got a plumber from rated tradesmen paid out twice as needed someone to correct their job! any advice would be very much appreciated
 
sounds like the pull switch or burnt terminations. do not use the shower. there is a serious fire risk there. if it's supplied by a breaker, then turn off the breaker. if a fuse, pull the fuse out. a sensible price for replacing the pull switch would be around ÂŁ80 - ÂŁ90. assuming everything else was OK.

if you post your location, there's probably one of us close enough to youm to sort it for you.
 
oh god im scared!!! my bathroom lights have been flickering these last two nights is it linked do you think? so sorry so sound so dumb but supplied by breaker?? fuse?? lost not sure what you mean sorry its just a plastic box attached to my ceiling with a little red light and cord? thanks for your reply
oh im in lancashire pr area...
 
You'll have a consumer unit aka distribution board aka fuse box that supplies all the circuits in your house. Identify which is the shower and either switch the circuit breaker off or pull the fuse. If in doubt there must be someone on here near you who can help you.
 
by PR, i assume preston.a bit too far for me to make it a fair and economical job. sure there's somebody nearer to you. your first main concern is not to use the shower till it's been fixed.
 
right ok yes theres a cuboard in my living room with electric box and black flick switches on its covered by a clear plastic case - must be this
will deff not use my shower till its been looked at
yes im chorley nr preston thankyou though for thought
 

Reply to shower tripping out in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
325
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
852
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

Similar threads

I
  • Article
No water in shower head, pressure/flow problem Dear Professionals, could you please advise. I have standard mixer tap in my bath (its about 15...
Replies
0
Views
122
IrinaPri
I
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top