Hello I have just installed a new fuse board and when the shower runs the MCB trips within 20-30 seconds
the ins rest is 1000+Mohms the ze is 0.54 ohms
the shower is 9.5kw I know I nees a 40amp breaker but what I cant understand is why it was ok on a 30amp wired fuse before
and it shouldnt trip out so fast even on a 32amp type b MCB
the rcd does not trip
any help would be great Cheers