Hello I have just installed a new fuse board and when the shower runs the MCB trips within 20-30 seconds
the ins rest is 1000+Mohms the ze is 0.54 ohms
the shower is 9.5kw I know I nees a 40amp breaker but what I cant understand is why it was ok on a 30amp wired fuse before
and it shouldnt trip out so fast even on a 32amp type b MCB
the rcd does not trip
any help would be great Cheers
 
Therein lies your answer.

Your shower is pulling near enough 40A

Put an ammeter round the line and see what you are actually pulling.

Dont forget that old 3036 fuses were able to go quite a way above their rating.
 
Last edited by a moderator:
If you get you red regs out and look at the current/time tripping curves for your mcb it should show you how long it will last at 40amps and as rewirable fuses have a different time curve they wont blow/trip at the same timings.
 
I had a similar problem today.

Simple CU swap.

Several lighting circuits quite a few LV downlights, no schedule.

Switched on all the lights to establish what MCB did what.

After a minute, one popped.

Got out the clamp meter and it was pulling around 6amps, through an old wylex NB 5A MCB.

A 40amp shower will not run on a 32A MCB.
 

Reply to Shower tripping in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
840

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top