Old Triton shower tripped RCD so I replaced today with new Triton shower.

Still trips RCD ( maybe old one wasnt faulty?)

8.5KW on Wylex B40 mcb, 6mm 6242yh ( but only approx 5mtr run ).

RCD & MCB hold untill I switch on at ceiling switch,then trips RCD but not MCB ( so earth fault not overcurrent).

Linked out switch same result,changed switch same result.

Cable is surface & shows no sign of damage.

Am not prof sparkie so no test equipment.

Do I need to replace the cable from the switch to the shower?

Can anyone advise?

Thanks in advance

Steve
 
Firstly one of the problems with showers is the pull switch so many cheap ones about and one of the biggest problems ive found is the termials burning out so id check there first , disconnect the shower circuit from the board and carry out all the tests as usual ,continuity the the IR right down to the shower and see if there are any faults ,one thing i would do if the cable is 6mm reduce the size of the mcb to 32 amp if the cable runs through the loft and covered in less that 100mm of insulation then the cable is only rated at 34 amps
sorry just red your post proprly have you got the L and n the wrong way round

also sorry to point out if you repace any cables it falls under Part P and the work is notifiable
 
Last edited by a moderator:
As said needs testing ! you can do continuity test from discon shower circuit test cpc-l with multimeter then discon switch and do same ! then same with n-e etc that should tell you what leg is at fault if not ir test needs doing.
 
i would check if its 8.5 kw at 230v or 240v sounds like your on the limit with 6mm cable i allways run a 10mm cable if the shower is above 7.8kw better safe than sorry mate ive seen loads catch fire
 
i would check if its 8.5 kw at 230v or 240v sounds like your on the limit with 6mm cable i allways run a 10mm cable if the shower is above 7.8kw better safe than sorry mate ive seen loads catch fire

Yer i have an 8.5 and at home and always install a 10 as gives me the option of uprating if i want without pulling tiles off ect to get to cable for rewire.
 
If its not cable then maybe RCD is faulty?? when you do the RCD test the first test you do is the nuisance tripping test so could it be this maybe.

How often does this occur I.E. a working RCD starts to fail mechanically?.
 

Reply to Shower trips RCD... in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
178
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top