I need a solution for a problem I have, just cant seem to think at the moment.

I need to shut off a 3 phase supply when a supply to one phase has failed? Now I am thinking 4 pole contactor, but I am not sure of how to monitor the 3 individual phases on 1 control circuit? 3 control circuits perhaps?
 
use 3 single pole contactors with the 3 phases operating a (A1&A2) coil each, with the L1&L2 contacts in each wired in series to control the coil in a 4 pole contactor. Does that make sense?
 
^ thanks DS

but I do think my OP has been awerserd by post no. 8

thanks guys


Can we let this run for a couple of of days, before a mod closes it down (happy with that), but pretty sure I have a good answer.

Thanks again hawk
 
Essentially, in its simplest form my drawing is what a phase faliure relay does :)

You don't neccessarily need a phase faliure relay so I'd go with whichever option is cheapest.
 
From the OP i'm still not sure what he's trying to do. If all he wants to do is shut down a 3 phase supply when losing a phase, say due to a fault down stream, and the supply has fuse over current protective devices, then all that's required is to replace the fuses with a multi phase MCB/MCCB. Anyway if he's happy that he's found a solution in the way of a phase failure relay, all's good!! lol!!


One of the reasons i don't like fuse protection for poly phase motors, unless those fuses are of the striker release type, where when any fuse ruptures, is releases a striker to disconnect all the phases.
 

Reply to Shut off 3 phase supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
613
You only need to switch the lines and the contactor is rated per pole so for example a 16A four pole contactor would be fine.
Replies
1
Views
280

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top