I

Inteificio

Hi,

A question that should be simple, is killing me.

I have literally been researching this for months for no result; so if anyone even knows someone who knows the answer; or somewhere I could get the info please help.

We are currently using silicone insulated wire at work, a lot of it.
This is the stuff regs say we should be wiring domestic boilers with.

The issue is I am not running it in free air with an ambient of 30!
I am running it in trunking with multiple circuits and an ambient up to 85 degs.

I have no clue how to rate it, which worries me.

The stuff we use is specifically SIAF, which is glass fibre coated silicone, it can take 140 deg conductor temp. The glass fibre is usefull because even if the silicone incinerates, the glass will hold it in place maintaining insulation (just don't expect to be able to bend it much afterwards)

If there is a way to rate SIAF that would be great, but that is quite specialist stuff, even the way of rating normal silicone wire would be great.

No one seems to know how to answer this, so even if you have a slight idea it would be a great help.
 
I have been asking this question for months and that is the first response I have got, you are a star.

That is a lot of the info I need, and I have a company to ask now!

I just need to know what they mean with their amp rating.
Is that at st&p, I need to know what it does at 85 degs, not 20.
What is the max acceptable conductor temp? is that the 140, or is that the max ambient to pull their listed amperage?




p.s. It gives you resistance, so you can calc volt drop for that
 
Hi Peter I have tried to dig out an old contact I had a eland but I think it must be in the UK. I have had several dealings with them mate and they have always been top notch so I'll guess their Tech Dept will be more than able to help you.

Yes mate if you have the load then you can work out the VD, Lol if I was honest P I didn't want to take it for granted you knew ohms law lol....sorry mate
 
Last edited:
"if I was honest P I didn't want to take it for granted you knew ohms law" - Quite a wise assumption, I am amazed the amount of sparkys I meet who do not know it.

I am a lot better at maths than electrics, so worry not if it gets complicated.
 

Reply to Silicone Insulated wire. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top