As the title suggests, I'm running a submain. The space in which I have to work at the supply end is extremely limited though.

The CU at the supply where the SWA needs to terminate is mounted on the inside of the external wall in the porch. Ideally, I'd just run the SWA through the wall and up into the CU, but as I said space is tight. It would be far easier for me to terminate the SWA into an adaptable box on the outside of the external wall and run a short length of T&E directly through the wall into or just below the CU on the other side (which is adjacent).

Technically this would mean there is an extremely short length of cable running through the wall at less than 50mm (which would suggest a need for RCD protection if we're only looking at the OSG). Lets look at the regulation concerned:

Reg 522.6.202:

"A cable installed in a wall or partition at a depth of less that 50mm from the surface of the wall shall ... comply with regulation 522.6.204"

Which states

"be provided with mechanical protection against damage sufficient to prevent penetration of the cable by nails, screws, and the like ..."

I can't see that a 100mm length of T&E running though and perpendicular to the wall, where the cable can be seen entering and exiting from either side, would ever be at risk at having a nail or screw damage it ...

Thoughts?
 
Last edited:
A cable going through a wall directly behind an accessory would not fall under "installed at a depth less than 50mm" IMO.

Why connect a piece of T+E to it ? Just gland into a box of your choice and run the cable inner through the wall. If you want to keep the metal containment/armouring aspect of the cable run continuous then pass the cable through a metal conduit where it penetrates the wall.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London

Thread Information

Title
Simple question regarding Non RCD protected SWA run from CU
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2
Unsolved
--

Advert

Thread statistics

Created
ZEDEZ,
Last reply from
ZEDEZ,
Replies
2
Views
1,691

Advert

Back
Top