With for example the Wylex NXHL1B Single Module DP range of RCBO's there is (at last) a sensible solution to RCD protection for all circuits individually, but only up to 40 amps. Is there a manufacturer doing 50 amp single module double pole rcbo's e.g for thirsty 10 kw or 11 kw large cookers and showers?
 
With for example the Wylex NXHL1B Single Module DP range of RCBO's there is (at last) a sensible solution to RCD protection for all circuits individually, but only up to 40 amps. Is there a manufacturer doing 50 amp single module double pole rcbo's e.g for thirsty 10 kw or 11 kw large cookers and showers?
New installation so not decided yet which board... so which ever one offers a 50 amp single module DP.
 
MEM, you get the rcbo pod and add what breaker size you like, even 63 amp
 
I find they trip when the oven gets older, the elements deteriorate and trip the RCBOs, I have lost count of call outs over the years where the oven is the reason, Obviously on a TT there is no avoiding this, but I would wire an oven and a fridge as well to the regs so an RCBO or RCD wasn't required if I could, JMO.
 
^^ interesting

I find it’s washing machines and dish washers that cause aggro.

Just yesterday our aged washing machine tripped the rcbo ... so to empty it I ran an extension lead from our fridge freezer socket (dedicated circuit mcb) ... and emptied it ......

Anyway a cooker on a rcbo isn’t an issue ..
 
I find they trip when the oven gets older, the elements deteriorate and trip the RCBOs, I have lost count of call outs over the years where the oven is the reason, Obviously on a TT there is no avoiding this, but I would wire an oven and a fridge as well to the regs so an RCBO or RCD wasn't required if I could, JMO.
Wouldn't that be all the more reason to put a cooker on an RCBO, that way if it deteriorates it's disconnected plus there's no nuisance to other circuits?
 
P.s. Just noticed my opening thread should have read " Wylex NHXS1" not Wylex NHXL1; These RCBO’s include switched neutral as standard.

This stops the old Neutral to Earth fault causing problems when fault-tracing as it provides full separation of circuits.

They do not however retrofit onto the "balcony " style busbars that were common in Wylex.

The new Regulation, 536.4.203 (devices and components that are used in low voltage assemblies, such as consumer units, must only be those that have been declared suitable for that purpose by the manufacturer of the assembly.Or put another way. Only use manufacturer approved parts, don’t mix brands of devices, or control items. Using unapproved parts will invalidate manufacturer guarantees and may result in an unsafe installation...) (see: www.electrium.co.uk/news/how-to-choose-the-right-consumer-unit-and-what-to-put-in-it) rules out mixing makes and vintage within a dist board. That all devices fit a standard din rail yet fits to busbar vary so much has always been a source of danger from poor contact overheating etc.

The fact that the new single module DP rcbo's are so compact hopefully does not impede their reliability... particularly in the case of 32 and 40 amp ratings? They have not been around long enough to know yet so this injects an air of caution about using them.
 
Wouldn't that be all the more reason to put a cooker on an RCBO, that way if it deteriorates it's disconnected plus there's no nuisance to other circuits?
I don't like any appliances on RCBOs, my kitchen ring is on a breaker, the other house sockets on a RCBO, and I have a seperate circuit for the fridge as well lol
 
I have metal conduit in the wall down to my sockets from the floor above, I agree with Murdoch about washing machines etc, they nusience trip, as do most appliances, I don't like RCBOs on kitchen appliances, and won't change my mind ;)
 

Reply to Single Module Double Pole RCBO over 40 amps? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
223
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
683
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
625

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top