daza1001

Hello All,

Today i am connecting up a single phase contactor.
I know the contactor needs a neutral to operate the coil, but does the neutral for the load have to run through the contactor as well? As you can tell I have not done to many of these.
The contactor is for the underfloor heating as it is drawing 19.5A & the programer is rated at 16A.

Many thanks
 
if the programmer is rated at 16 amp then no more the 16amp should be switched via that programmer
You could use the programmer to switch contactor which would then switch the required load
I always switch my live and neutral via the contactor ie 2 pole or 4 pole depending on number of phases
 
Hello Ashrow,

That is what we have done. But a mistake was made when the cables were 1st fixed & 1 cable less was pulled from the programer to the contactor than required.
So I was hoping we could do away with running the load neutral through the contactor that then gives us enough cable cores.

Hope this makes sense.
 
if the programmer is rated at 16 amp then no more the 16amp should be switched via that programmer
You could use the programmer to switch contactor which would then switch the required load
I always switch my live and neutral via the contactor ie 2 pole or 4 pole depending on number of phases
i wouldn't switch the 3P and N through a 4-pole
i'd use a solid link for N myself
 
it is always a good practice to switch both line and neutral through the contactor. but if you can't do it, then just switching the line will be acceptable. just as an afterthought..... you have a N for the coil. can you not use this to feed a N pole on the contactor?
 
Telectrix,

If I used the neutral from the coil cct this has been fused down to 13A so would this still work?

Thanks

the N is not fused down, as tony pointed out. all down to if the N cable is of sufficient size to carry the 19.5A (+ a little bit for the coil).
 

Reply to Single phase contactor in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
372
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I think it was too early yes I meant 3 not 2, but great I'll give that a whirl and thanks.
Replies
8
Views
521
I really can't see a problem with it assuming there is a neutral there.
Replies
6
Views
689

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top