Hi Everyone
I would be glad if you could clarify this for me:
For a Load Estimate Survey whereby 95% is single phase, the Load Estimate is 90 KVA (Single Phase). However, the power supply is three phase 4 wire system.
To calculate the current per phase, the 90 kVA is divided by three i.e. 30 kVA per phase. Hence, current per phase is (30 x 1000/230) = 130 A/ph.
Hence, the 90 kVA single phase is equal to 90 kVA three phase??? This is where I'm confused.
In addition, to undertake a load estimate survey, which is better to workout all the currents or use the kW or kVA ratings with Utilisation factor & simultaneity factor.
Thanks in advance.