I am currently doing some periodic inspecting to domestic properties and have gone into 2 properties which seem to have an overload problem. The both have 28 way split load boards supplied via a single phase supply and protected by 100a main BS1361 fuses.

On the boards are approx 6 lighting circuits, 7 showers, 2 cookers, 4/5 ring mains and the odd water heater, smoke alarm circuit. Obviously the max demand is above 100a.

Has anyone got any advice on what I should do in this situation prior to issuing a satisfactory report??
 
Hi Pete.

Well technically if they are 25mm tails protected by 100A fuses then there isn't really anything wrong.

I would suggest an accompanying letter to the PIR, explaing the situation with regard the demand of the installation and perhaps investigate the possibility/cost of installing 3 phase, but as long as all circuits are fused correctly and as I said the tails are of the correct size for the overcurrent protection then I dont see how any of the codes can be issued.

Others may take a different view.
 
im with lenny on this one. In the letter i would make a big point of saying if the main fuse went then the whole building will be without electrics. (it covers your --- and if you quote for the works you might get it)

Ash
 

Reply to single phase or 3 phase supply?? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
763
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
765

Similar threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
605
Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
602

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top