hi

I'm having a problem with an RCBO tripping out and it is unlikely to be a N-E fault. I suspect the associated neutrals have been terminated into the wrong RCBO even though there is no load connected as all the RCBO's feed unused sockets. The board itself is 3 phase and I am wondering if this alone is enough to trip the RCBO'S.

Can anyone advise, thanks.
 
Why isit unlikey to be a N-E ?

Unused sockets - apart from the spur the builder did feeding a perm connected fridge or whatever that mr.client forgot to mention.

Follow the testing procedures...you'll get to the bottom of it, perseeverance my son :)
 
You can prove your theory by plugging a load into all the other sockets 1 at a time and see if any Rcbo trip.

However it's easy enough to prove the neutral is wrong in the problematic Rcbo.
 
Why isit unlikey to be a N-E ?

Unused sockets - apart from the spur the builder did feeding a perm connected fridge or whatever that mr.client forgot to mention.

Follow the testing procedures...you'll get to the bottom of it, perseeverance my son :)

You need to do what I do now on here... Assume people don't know how to test, or fault find. that's the way this forum and the industry is going!
 
Its a very basic question which shows a lack of knowlege.
Are you an apprentice,new tradesman or maybe a electrical trainee?
You are not getting much help here because it is so basic and on the off chance you are a Electrical Trainee, nobody will help.
If you were to explain something like, always did domestic sparky work and not sure about tp&n, maybe you would receive more help.

Boydy
 
If your unsure the correct Neutral is in the RCBO then very basic testing can clarify this... im sorry but just asking such a question means you are not competent, this should be in the DIY section and TBH DIYers shouldn't be delving into 3ph systems IMHO.
 

Reply to single phase RCBO'S on a 3phase board in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
921
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top