Morning all,

Little advice regarding whether spuring from a Three phase isolator to a single phase FCU is allowed?

I need to wire a Single phase FCU which is located right next to a 16A TP isolator to a high speed door. Obviously, It would be a lot less pain to wire straight from the TP isolator to a SP FCU. Rather than running a cable from the Sub main for the FCU.

Anyone have any objections? I know it's not ideal. However, via a regulations point of view I can't find anything against this practice.

Cheers.
 
the TP circuit will have been designed for the size of load across the 3 phases for that piece of equipment....

to then add a SP load off one of the phases at that point may overload that one line out of the three.
 
the TP circuit will have been designed for the size of load across the 3 phases for that piece of equipment....

to then add a SP load off one of the phases at that point may overload that one line out of the three.

TP circuit is fed from a C16 MCB with the FLC of the high speed door at 6A/phase. The SP FCU will power a security roller door which has a FLC of 6.5A. Realistically both doors cannot be used at the same time as the security roller door must be opened first before the high speed door will operate.

Hope that makes sense.
 
Think about it this way: if you had a 3Ph supply running to a small 3Ph DB which had a 3P MCB in it feeding an occasional device and the DB had 3 x 1P slots available, would you be posting the question?
 
Funnily enough I was on a job the other day where they had 2 roller shutter doors (3ph) on the same 10A supply, one effectively 'spurred' off the other.
Circuit cabling 2.5 so never going to be overloaded and whilst not sure of the flc, overloading of the mcb wasn't an issue the mcb had not been reported as tripping (it wasn't what I was on site for).
So no not ideal but no objections, its just another radial circuit!
 

Reply to Single phase spur from Three phase isolator. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Agree with Dave disconnect unused Phases on the outgoing side of the isolator. No reason to replace mcbs with single pole, unless you need room...
Replies
2
Views
1K
  • Question
Ok Dave thanks, no more accidents yet 🙏😂….
    • Like
    • Informative
    • Winner
Replies
6
Views
2K
Do you recon this is three phase in? And any idea what the beasty grey metal box is?
Replies
7
Views
1K
  • Question
I would personally leave it, a Ryfield or MEM Exel replacement would be consideral expense plus a replacement would/may require additional rcd...
Replies
8
Views
2K
  • Question
I'm very similar mentally. When faced with a tricky fault I usually break out the crayons, it helps to visualise problems.
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks