Why must single pole devices be fitted in the phase conductor? I understand that polarity must be assured through out the circuit but is it a bit more in depth than this?

Thanks.
 
Hi single pole devices must be fitted in that way for safety uniformity and compliance with the BRB have a look at 132.14 on page 18 of said BRB.


Hope that helps.



Chris
 
Imagine what would happen if the switch was in the neutral conductor on a socket outlet ..... the live would still be connected to appliance even when switched off... dangerous. HTH
 
Because if you did'nt switch the live or should I say line then you would'nt really be switching the circuit / equipment off ' circuit / equipment would still be live but the neutral return would be disconnected.
- in laymans terms -
 
Thanks for the replies. A few mins after I posted the question the answer became obvious. Turn the switch off but the light fitting would still be live, not good! Especially if you went to change an Edison. Thanks again though.
 
single pole devices must be installed in the phase conductor as this is in-line with the protective device

incorrect polarity would stop the flow of current through the neutral but would not effectively isolate the device/circuit/equipment as a potential voltage would still be present.
 

Reply to single pole devices in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
153
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
518
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
459

Similar threads

I'm now in West Virginia but my wife and I also own a home in the Philippines. The current in our province is 240v, but single pole. I have...
Replies
0
Views
191
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
604

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top