Situation.

Domestic TNS

Main consumer unit fed direct to incoming.

it has an upfront single pole RCD works fine. No main switch. No double pole isolation available.

Is this a potentially dangerous situation due to single pole Isolation?

I feel I can’t bring myself to give a C2 on an EICR, but equally I want to Tell customer to remedy this.

also it’s a Hager RCD in a steeple board, but the fit is good so was not going to code that.

bad design. Yes. But bad Design isn’t worth a code.
 
When I tripped the RCD the line to neutral on the supply side obviously 230:volts.

on other side obviously no voltage.

but between incoming live and neutral on the other side 230volts,

so came to the conclusion the neutral was open.

however ive just realised what a berk I am of coarse the neutral on the inside is connected to the neutral bar which in turn is connected to multiple circuits some of which will have natural and designed earth leakage. Thus an alternative path to earth.
 
I was getting full 230 volts.
Interesting, that is beginning to sound a bit more serious.

While I would very much doubt that an incomer style RCD would be single-pole switching, it is not beyond possibility that one pole has stuck.

I guess you could check for N-E faults on the installation (though I would expect that to be RCD-tripping if an actual short and not a few kOhm or similar from wet dirt).
 
Interesting, that is beginning to sound a bit more serious.

While I would very much doubt that an incomer style RCD would be single-pole switching, it is not beyond possibility that one pole has stuck.

I guess you could check for N-E faults on the installation (though I would expect that to be RCD-tripping if an actual short and not a few kOhm or similar from wet dirt).
my Bad my approved voltage indicator is just reading extra low voltage. just lighting up,the 12V led .

Your spot on right.

i heard the continuous tone saw lights on voltage indicator light up and presumed it was 230V.
 
Think your right. Just hav8ng a blonde moment.
Found it, although it may not apply here

462.1.201
A main linked switch or linked circuit-breaker shall be provided as near as practicable to the originof every installation as a means of switching the supply on load and as a means of isolation.

A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt
both live conductors of a single-phase supply
 

Reply to Single pole up front RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Maybe wonder full pc 1966 or LN with is wonderfull diagrams showing apprentice how it should be done regarding TT to the outer building...
Replies
7
Views
3K
Indeed. I would agree with this. Why anyone would think this was a good idea....
Replies
6
Views
6K
loz2754
L
Hi, My probe was on the outgoing neutral of the RCBO. I will be testing again this week so I will play around, many thanks for your reply.
Replies
7
Views
4K
It seems fair enough. (If you stuck the 2nd unused 32A socket feed in the cpc bar I think the first DB would be way under the CCC of the supply...
Replies
14
Views
3K
  • Question
This looks like a decent project to get your teeth into. It may be worth your while looking through the directory on here for your area as your...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks