3 brass bushes on db ,12 circuits ,live going through bush 1, neutrals through bush 2, cpc through bush 3 , anything in regs about eddy current ,4mm single cores
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss singles in brass bushes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
brass bushesWhat material are the bushes in?
yes it is allowed or no its notYes mate can't remember the reg. no. but all lives through same entry into ferrous enclosure.
brass bushes
brass bushes ,bushed onto metal trunkingWhat they are just floating in mid air are they?
Someone decided to thread some cable through the bushes because they thought the cables needed brass accents?
can see regs about single core armoured cablesI meant yes there is something in the regs, which was the question you asked.
Also that all live conductors must go through the same entry into a ferrous enclosure.
I thought that I had answered the question!
It is NOT allowed to put lives and neutrals through separate entries into a ferrous enclosure.
no slot cutHas a slot been cut in the metal trunking, joining the holes?