I have a run to a 9.5kW shower. Prefer not to disturb the ceiling (flat roof above) and am thinking about using mini-trunking round tops of walls, then down to shower.

Small mini-trunking would be great, but I know I'm going to have fun with 10mm T&E in small trunking - so I'm wondering whether I could use singles instead. I don't see any reason why not from the regs.

It's only about a 12m run, so to save cost I'm thinking of using some existing 10mm T&E I have - strip that down to get the L and N singles, then buy some 6mm CPC insulated single.

As far as I know there's no difference between the 10mm insulated conductor inside a piece 10mm T&E, and a 10mm single.

Anyone see any flaws in the plan to use mini-trunking for singles - or stripping T&E to get a single? Or should I bite the bullet and put the T&E through the ceiling?

(Cable is coming off a 40A mcb on 30mA RCD, by the way, and shower feed is nicely bonded up.)
 
Absolutely nothing wrong in using singles in mini trunking, just make sure you use a big enough one.

And there is noting wrong in stripping some T + E to run it in, though not sure why as you can run the T + E inside the trunking itself and do away with the hassle of stripping it and the need to buy 6mm G/Y singles. The only advantage is in singles you maybe able to use a smaller than 6mm CPC, so save cost on material.

Also if you use singles you would need to run that trunking from the CU along the entire length of the installation, which could be fiddly, whereas in the CU cupboard if you used T + E you could clip and when you enter the area where the trunking is to be used just enter the cable into it.
 
Many thanks, Malcolm. The thinking behind singles in mini-trunking was there are 4 90 degree turns, so I was thinking it would be easier than getting 10mm T&E to do that. Good point about need for trunking all the way from CU, but I'm thinking of clipping T&E from CU to 50W isolator pull switch, then singles in the mini-trunking from there to shower.
 
Many thanks, Malcolm. The thinking behind singles in mini-trunking was there are 4 90 degree turns, so I was thinking it would be easier than getting 10mm T&E to do that. Good point about need for trunking all the way from CU, but I'm thinking of clipping T&E from CU to 50W isolator pull switch, then singles in the mini-trunking from there to shower.

Hope that is a 50amp one lol.

If your doing this in trunking and singles you know you could get away with 6mm cable as that will give you 41amps
 
Presumably your planning to use MT2? Personally, If I was going down that route, I would just stick MT3/MT4 and do it in 10mm as I think your pretty close to the limit with 6mm (although I apprichate still within). Aslong as your firm with 10mm2, you'll get it to do as you wish.

Rich
 
Presumably your planning to use MT2? Personally, If I was going down that route, I would just stick MT3/MT4 and do it in 10mm as I think your pretty close to the limit with 6mm (although I apprichate still within). Aslong as your firm with 10mm2, you'll get it to do as you wish.

Rich

In this heat you're probably right, Rich! ... .putty in my hands ... still, I'd prefer mt2 to make the down section to shower as 'invisible' as possible.
 
Why not MT3 or 4 for the horizontal run and MT2 for the vertical run to the shower unit. You will be able to make the 90[SUP]o[/SUP] bends in 10mm[SUP]2[/SUP] T+E inside the larger trunking without to much difficulty.:)
 
well its over 10m in length ,do you need inspection section?????????? or is that just conduit. and with four 90 degree turns, i think that limits what size of trunking you use, im just picking this out from all the information ive took in last few years. could be off me rocker and full of it, but il take it like spark
 
how did you get on in the end? i've got a shower to do in trunking and i'm not happy bout it, dont like the idea of water/condesation running down a vertical drop of trunking into the shower, how doe it get made of is it okay?
 
how did you get on in the end? i've got a shower to do in trunking and i'm not happy bout it, dont like the idea of water/condesation running down a vertical drop of trunking into the shower, how doe it get made of is it okay?

The provided cable entry on showers is a channel designed to allow water to enter and drain safely....just make sure you use that and dont cut your own entry to suit.
 

Reply to Singles in mini-trunking in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
936

Similar threads

  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
834
  • Question
I think a 3 legged breakout boot would be your best bet in the circumstances.
Replies
3
Views
603
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top