I have a old fuse board and a new RCD C.U which are connected through a Henley block my main earth is 16mm and my main bonding is 10mm all going into MET the new CU which is a 4 way is connected to the MET by a 10mm C.P.C and the old fuse board is connected by a 6mm C.P.C does both these C.P.C have to be upgraded to 16mm
its TNCS by they way

second my old fuse box 60amp has 16mm tails is this ok or need upgrading to 25mm
 
I would upgrade the the 6mm to at least a 10mm because you are TNC-S if its a old fuse board you may stuggle to get a 16 mm in.

Your bonding is fine at 10mm

16mm tails are also fine for 60 Amps
 
Because your system is TNC-S your bonding is going to be based on your DNO neutral.
So if the neutral is 35 mm or less 10 mm is required.

Your earth conductor can be calculated with the adiabatic equation but has to be 10mm or more due to the PME.

If you want a calculation done post the ZE at the origin of the instalation!

Hope this helps.!!!!
 

Reply to the thread, titled "size of C.P.C" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
size of C.P.C
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
3

Thread Tags

Advert

Thread statistics

Created
coatesykid,
Last reply from
tony mc,
Replies
3
Views
2,323

Advert

Back
Top