C

coatesykid

I have a old fuse board and a new RCD C.U which are connected through a Henley block my main earth is 16mm and my main bonding is 10mm all going into MET the new CU which is a 4 way is connected to the MET by a 10mm C.P.C and the old fuse board is connected by a 6mm C.P.C does both these C.P.C have to be upgraded to 16mm
its TNCS by they way

second my old fuse box 60amp has 16mm tails is this ok or need upgrading to 25mm
 
Because your system is TNC-S your bonding is going to be based on your DNO neutral.
So if the neutral is 35 mm or less 10 mm is required.

Your earth conductor can be calculated with the adiabatic equation but has to be 10mm or more due to the PME.

If you want a calculation done post the ZE at the origin of the instalation!

Hope this helps.!!!!
 

Reply to size of C.P.C in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
949
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
612

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top