Hyperthetically.
TN-C-S in a Domestic - Earthing Conductor 16mm. Bonding conductors 6mm. I understand that the bonding conductors must be not less that half the earthing conductors meaning the the 6mm bonding in this situation is too small but they are a pain in the backside to change. However if I apply the adiabatic to the earthing conductor I can get away with a smaller size. So I reduce the the Earthing conductor to 10mm and I am now compliant.
Is the installation more safe or just more compliant?
TN-C-S in a Domestic - Earthing Conductor 16mm. Bonding conductors 6mm. I understand that the bonding conductors must be not less that half the earthing conductors meaning the the 6mm bonding in this situation is too small but they are a pain in the backside to change. However if I apply the adiabatic to the earthing conductor I can get away with a smaller size. So I reduce the the Earthing conductor to 10mm and I am now compliant.