Okay chaps, I need a dispute settled so thank god that he created the iPhone. How do u work out the size of the bonding to the gas and water in an industrial premises? Any takers please

Cheers

Moosey
 
on a power station i jsut finished on, evertything was a minimum of 70mm2 and theyb ran 240mm2 bare earth along all of the ladder rack! slightly over the top!

dont know about your situation though matey. Isnt there guidance in a guidance note, installation designers?
 
According to Section 544 in the BRB;
If not PME The cross sectional area of a bonding conductor need not exceed 25mm2, but if PME on site then a bonding conductor shall be selected according to the largest neutral conductor.

Table 54.8 ~ Where PME conditions apply

Copper equivalent cross sectional area of the supply neutral conductor in relation to Minimum copper equivalent cross-sectional area of the main protective bonding conductor
35mm2 or less = 10mm2
35mm2 up to 50mm2 = 16mm2
50mm2 up to 95mm2 = 25mm2
95mm2 up to 150mm2 = 35mm2
Over 150mm2 = 50mm2
 
Last edited:
Cheers notsosmart, I thought it was to do with the neutral supply conductor and I was sure 50mm was max. It's a factory with a supply transformer on site I take it that rule applies then...

Cheers
 

Reply to Size of main bonding in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
186
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
573
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
525

Similar threads

  • Question
UPDATE, after contacting Paypal, uploading all the emails and evidence the sending the transformer back I have now received a full refund...
Replies
6
Views
2K
I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
911

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top