I posted the other day regarding advice on a switceh fuse for when the CU is a distance from the meter.

I've decided on using a 60amp switch fuse which will be fed with 25mm tails. From the switched fuse to the CU, roughly 9-10 meters, I have specced 10mm 2 core SWA and a 16mm earth. The supply is TN-C-S, so have specced the earth to match that of the tails at the meter, rather than the size of the SWA.

Is this the way in which the regs describe sizing if the main earth. or should the earth be sized on the SWA and not the supply tails.

Maybe quite simple to some, but would like other opinions on it:eek:

Thanks
 
How much more would it have been just to make the SWA a three core 16mm?:) woops sorry seen your other thread didn't realise the bonding will go back to the main head MET. 10mm three core SWA for me then 16mm from switch fuse to MET but as telectrix says future proofing 16mm 3 core could still be an option
 
Last edited by a moderator:
How much more would it have been just to make the SWA a three core 16mm?:) woops sorry seen your other thread didn't realise the bonding will go back to the main head MET. 10mm three core SWA for me then 16mm from switch fuse to MET but as telectrix says future proofing 16mm 3 core could still be an option


Gas bond will be run to the head MET, but water will be connected via earth bar in the CU.

One of those jobs i htink where customer is old, wants to spend as little as poss so couldn'r care less about anyone who comes in after them.

Thanks for the input:cool:
 
Gas bond will be run to the head MET, but water will be connected via earth bar in the CU.

One of those jobs i htink where customer is old, wants to spend as little as poss so couldn'r care less about anyone who comes in after them.

Thanks for the input:cool:

I can picture the customer right now;) 16mm 3 core SWA for me then, when I was after a load of SWA one of the guys put this link up really competitive prices if I remember

https://www.electriccableco.com/electric-cable-shop.htm
 
Last edited by a moderator:
Gas bond will be run to the head MET, but water will be connected via earth bar in the CU.

One of those jobs i htink where customer is old, wants to spend as little as poss so couldn'r care less about anyone who comes in after them.

Thanks for the input:cool:

Technically you shouldn't do that mate. As there can only be one MET and bonds have to go back to that. What you saying is you will have 2 one at the head and the other as the earth bar of the CU.

Plus also mate would not advise using where the DNO link as YOUR MET as that is theirs. I know you see it quite a lot but usually the DNO can get a little upset with that.

If it were me mate, I would fit a MET at the header, bring the earth conductor from the TNC-S into that. Then run your bonds back to it, and the CPC for the CU. Or the other way round the MET at your CU and run the bonds back to there.
 
Technically you shouldn't do that mate. As there can only be one MET and bonds have to go back to that. What you saying is you will have 2 one at the head and the other as the earth bar of the CU.

Plus also mate would not advise using where the DNO link as YOUR MET as that is theirs. I know you see it quite a lot but usually the DNO can get a little upset with that.

If it were me mate, I would fit a MET at the header, bring the earth conductor from the TNC-S into that. Then run your bonds back to it, and the CPC for the CU. Or the other way round the MET at your CU and run the bonds back to there.

It may be slightly easier to run a new length of 10mm from the gas to the new CU position and make that end the main MET. I'm only guessing that the water is in the house and may be a pain to rewire back to the head in the garage, as opposed to the gas which will only have to be clipped along the garage then pop through into the CU. Sorry might be well out with my assumption
 
It may be slightly easier to run a new length of 10mm from the gas to the new CU position and make that end the main MET. I'm only guessing that the water is in the house and may be a pain to rewire back to the head in the garage, as opposed to the gas which will only have to be clipped along the garage then pop through into the CU. Sorry might be well out with my assumption

You may be spot on Pennywise but technically you can't have the bonds at 2 different MET.
 
Technically you shouldn't do that mate. As there can only be one MET and bonds have to go back to that. What you saying is you will have 2 one at the head and the other as the earth bar of the CU.

Plus also mate would not advise using where the DNO link as YOUR MET as that is theirs. I know you see it quite a lot but usually the DNO can get a little upset with that.

If it were me mate, I would fit a MET at the header, bring the earth conductor from the TNC-S into that. Then run your bonds back to it, and the CPC for the CU. Or the other way round the MET at your CU and run the bonds back to there.

Cheers Malcolm.

On every TN-C-S, I put a 4 way earth terminal near to the head and link the DNOs terminal to this. Never hook it all to the DNO terminal, never room anyway.

It may be slightly easier to run a new length of 10mm from the gas to the new CU position and make that end the main MET. I'm only guessing that the water is in the house and may be a pain to rewire back to the head in the garage, as opposed to the gas which will only have to be clipped along the garage then pop through into the CU. Sorry might be well out with my assumption

Gas meter is in the garage on opposite wall to the supply head. Water is in the house as you enter the kitchen. Will have to bring the water bond past the CU on the way back to the MET at the supply head then
 
You may be spot on Pennywise but technically you can't have the bonds at 2 different MET.


Sorry mate I totally agree with what you say, all I was saying was it maybe easier to take both gas and water bonds to the new CU position rather than having to reroute the water bond back to the head. cheers
 
You may be spot on Pennywise but technically you can't have the bonds at 2 different MET.

So lets say he carries a 16mm from the incomer to the cu and runs a 10mm for the gas to the cu and a 10mm for the water back to the incomer and labels then both. Its all part of the same installation, what is wrong with that? not a dig but a genuine question? where does it fall foul of the regs?
 
So lets say he carries a 16mm from the incomer to the cu and runs a 10mm for the gas to the cu and a 10mm for the water back to the incomer and labels then both. Its all part of the same installation, what is wrong with that? not a dig but a genuine question? where does it fall foul of the regs?

Somewhere in the installation you need a MET as to reg 542.4.1. If you taking the 16mm from the head to the CU then your earth bar in the CU is now classed as your MET.

That 16mm is the earth conductor from the DNO's earth point. It would be like say on a TN-S system if a BS 951 was fitted to the sheath, you can not class that as the installtion MET, and I don't think you would take a bonding cable back to connect onto it, as that is external to the installtion. The same as the earth rod of a TT system. all these are external to your installation.

Not sure if I explained that to well lol but hope you get what I mean.
 
Malc

The job I'm on, we have a Main Earth Bar with a removal link (for testing) All the Main Bonding Cables Terminate here.

Main Earth 70mm, Main Bonding Conductors 50mm, Earths to Dis-Boards Via SWA Sheaths Connected to Main Panel Casing, which in turns Connects to Main Earth Bar.

Main Panel Connects to Main Incomer.

How many Main Earth Terminals/Bars now?
 

Reply to Size of tails, SWA and earth size. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
612
loz2754
L
Hence the former name for TNC-S, PME. Protective Multiple Earth.
Replies
5
Views
660

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top