Hi Everyone
May be someone could shed some insight on the sizing and provide some suggestions:
3 phase Generators (400 V, 50 Hz) have the ability to sustain 250% kVA of its rated kVA at 30% voltage dip.
Suppose a machine needs to be powered by a standby generator during a power outage. It has 3 Nos. motors that start simultaneously as follows:
1 No. 11 kW (Start via VFD)
1 No. 2.5 kW (D.O.L)
1 No. 2.5 kW(D.O.L)
The Diversity Factor is 1
The Start kVA (11 kW motor) = 1.6 x (kW/ starting P.F) = 1.6 x (11/0.8) = 22
The Start kVA (2.5 kW motor) = 8 x (kW/ starting P.F) = 8 x (2.5/0.7) = 29 kVA
The Start kVA (2.5 kW motor) = 8 x (kW/ starting P.F) = 8 x (2.5/0.7) = 29 kVA
Total Starting kVA = 22 + 29 +29 = 80 kVA & Running kVA about 22 kVA (including lighting)
1. Since the Generator can sustain 250% of its rated kVA for 10 seconds, can a 50 kVA Generator rating be selected as all the motors will be started in less than 10 secs.
2. Someone who is used with generator sizing maybe could provide the multiplying factors for VFD, soft starter, DOL, and Star-delta, and a good insight of generator sizing for the above.
Regards
May be someone could shed some insight on the sizing and provide some suggestions:
3 phase Generators (400 V, 50 Hz) have the ability to sustain 250% kVA of its rated kVA at 30% voltage dip.
Suppose a machine needs to be powered by a standby generator during a power outage. It has 3 Nos. motors that start simultaneously as follows:
1 No. 11 kW (Start via VFD)
1 No. 2.5 kW (D.O.L)
1 No. 2.5 kW(D.O.L)
The Diversity Factor is 1
The Start kVA (11 kW motor) = 1.6 x (kW/ starting P.F) = 1.6 x (11/0.8) = 22
The Start kVA (2.5 kW motor) = 8 x (kW/ starting P.F) = 8 x (2.5/0.7) = 29 kVA
The Start kVA (2.5 kW motor) = 8 x (kW/ starting P.F) = 8 x (2.5/0.7) = 29 kVA
Total Starting kVA = 22 + 29 +29 = 80 kVA & Running kVA about 22 kVA (including lighting)
1. Since the Generator can sustain 250% of its rated kVA for 10 seconds, can a 50 kVA Generator rating be selected as all the motors will be started in less than 10 secs.
2. Someone who is used with generator sizing maybe could provide the multiplying factors for VFD, soft starter, DOL, and Star-delta, and a good insight of generator sizing for the above.
Regards