thegasguy

Hi all, I have been asked to run a 3 phase supply from a nearby service head to a new DB servicing a solar array to be fitted on a riding school roof.
This is to take the electricity generated back to the grid. A proper MCS contractor is doing the array.
The problem I have is that the array is rated at 50KW peak( at 230v) which I make 200 amps plus!
The sevice head is a standard 100 Amp supply.
How can I (1) be sure the existing incomer is not going to be overloaded and (2) work out the size of 4 core armoured needed to link the service head to the new DB where the installers will make their connection?
The solar boys don't want to know about anything beyond their final 'box'
Thanks,
thegasguy
 
I calculate 50kW as 72A per phase with 3 phases.

The solar people must spec the cable for you because if you decide the size and then there are voltage drop issues and the inverters cut out regularly then you will have an argument on your hands.
 
Last edited:
Thank you BruceB, I agree on 72A per phase max load.
The solar people seem strangely unable to calculate cable sizing! I am digging into who designed the system today, and whether they know what they are doing.
This reply may come from "tonyblud" (me as well) as I can't get into the forum this morning as 'thegasguy' for some odd I.T. reason. I have emailed 'Dan' at the forum to help me get back in.
Thanks again.
 

Reply to sizing 3 phase supply to/from 50KW solar array in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

As above, the DNO have many factors to consider when allowing power export, not just the current carrying capacity of their network but also if it...
Replies
3
Views
2K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
660
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
I'd advise checking their feedback first. It's about the worst I've ever seen on ebay!
Replies
1
Views
839
  • Question
We use one from Stephill generators, it covers the while check / switch / return sequence and included a charger to keep the generator's battery...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks